steam heat sizing
KirbyJ
Member Posts: 1
I am confused by the sizing tables in the Lindhart guide to steam heating. I have two radiators that share one 1 1/2" pipe, and then branch to each radiator with an 1 1'2"X1 1/4" X 1 1/4" tee. The 1 1/2" pipe branches off of the 2" main horizontally and then goes up vertically to feed the two radiators. Would this be considered a runout or an upfeed riser? The EDR of the two radiators are 96 and 30. If I go by the runout column then the one radiator by itself is too big for that pipe and the tapping on it is only 1 1/2". Thanks for any input.
By definition
a runout is the piping that connects a radiator to a riser..a springpiece connects a riser or first floor radiator to a main..people dont use the term springpiece much anymore..definition is from page 90 of the Dunham application manual 1953.gwgillplumbingandheating.com
Not sure
I think you would consider that an upfeed riser.0 -
Springpiece
Sounds like something a young guy goes out looking for after shaking off the winter doldrums. ;-)
I've heard them called take-offs, runouts (incorrectly, apparently) and upfeed branches (from Hoffman's Steam Heating Systems HS-901 A).Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240
- 120 Geothermal