Bostick84
Member Posts: 1
I have an old heater, model #KKH-14 and I need to know what the BTU's are on it so I can replace the unit with a new model of similar size. Any help out there? Thank you!
0
Comments
-
Someone professional may have the answer to your question.
Let me suggest, however, that a better solution if you have a hot water system is to calculate the heat loss of your building and from that, determine the size of the boiler you need. If you have a steam system, calculate your radiation and from that, determine the size of the boiler you will need.
When I got a new boiler, my old one had a Beckett oil burner in it rated at 70,000 BTU/hour. I could use larger nozzles to increase the firing rate, but never did that. When I calculated the heat loss of my house, I got 30,000 BTU/hour. A 70,000 unit would be over twice the size I needed.
I had to settle for an 80,000 boiler anyway because that was the smallest boiler my installing contractor had to offer of the mod-con type.0 -
Bad news...
http://www.heatinghelp.com/forum-thread/64663/Hydronic-Heater-Unknown-Make#p746576
Looks like its time for a new toe kick space heater...
ME0
This discussion has been closed.
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements