Buderus - Riello keeps shutting off
kennebago
Member Posts: 2
I recently had a house remodeled and had a Buderus G115 with a Riello FB5 installed. House is in Maine. The system generally works well but several times the burner has either shut done or failed to s take long for the house to cool down tart when heat was called for. The burner started when the reset was pushed, but i am very concerned. It gets pretty cold in Maine and it doesn't take long for the house to cool down. The flue is stainless and there is no barometric damper. I am a homeowner and an engineer. I have built several houses, and installed old style boilers, but I know nothing about this. I had the boiler installed by a local P and H guy but he seems a little lost -- anyone have any suggestions
thanks
thanks
OOPS !! Forgot, this is an oil fired setup
I forgot to add that this setup is oil fired0 -
Check
the install against the manual. Is it installed correctly? Was a heat-loss done? Is the unit sized correctly? What faults are coming up? Was a combustion analyzer used to set up the burner, and do you have a copy of the final results?0 -
OK
This is just a boiler with an oil burner. You need to get someone that can troubleshoot the burner. I thought it was a mod/con. I don't understand why your installer is lost.0 -
Buderus
Not a big fan here, but all that aside, It sounds like it is a direct vent boiler if there is no draft control. If not, then installer is clueless as to which model he installed. I would track the installer down. I'm sure this was not a freebie.0 -
Bill you prob....
right. The BF5 was the other clue that its a Direct vent. They can be very finicky. The combustion number done on set up have to be just right. Was the boiler set up? I mean did the installer get out a combustion test tool and check that all the settings were perfect? Is there a test slip there?0 -
chimney or direct vent
I've worked on BF5 burners in Buderus that were plugged into old unlined brick chimneys. Some work best with a draft regulator(sized) added, others work best with the set up specs for a F-series. The worst cases require the burner model changed to a chimney spec'd model. Usually depends on airtube insertion and what overfire and breech draft are.There was an error rendering this rich post.
the other issue...
w/ direct vents is that you can set them up w/ one outdoor temp and be all good. Then along comes a real cold day.. cold oil and really cold intake air changes the way oil atomizs... bang, sooting and lockouts. A nozzle heater helps.0