hot water baseboard
johnny1234
johnny1234 Member Posts: 11
just figured i need 119 feet off baseboard for a house im building thats 119x600=71,400 btus in how big a boiler do i buy????
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,584
    Question?
    How do you know you need 119' of baseboard?
  • johnny1234
    footage = how big a boiler
    sized room by room lxwxhx10=btu's divided buy 600=footage....added all together comes to 119 feet element
  • furnacefigher15
    furnacefigher15 Member Posts: 514
    What
    Method is that?
    L x W x H = cubic feet x 10 / 600 ?
    Where did that come from?
  • furnacefigher15
    Oh I see
    it now
    10 btu per cube and
    600 btu per foot emitted.
    I still don't know where the 10 btu comes from.
  • johnny1234
    what size boiler
    also found this http://www.bgmsupply.com/calculateheatloss3.asp
  • johnny1234
    what size boiler
    also found this http://www.bgmsupply.com/calculateheatloss.asp
  • johnny1234
    baseboard heat
    this house is 300sq. feet 72,00btu's required to heat just sounds low ...am i wrong
  • johnny1234
    baseboard heat
  • johnny1234
    baseboard heat
    this house is 3000sq. feet 72,00btu's required to heat just sounds low ...am i wrong
  • johnny1234
    baseboard heat
  • johnny1234
    baseboard heat
  • johnny1234
    baseboard heat
  • icesailor
    icesailor Member Posts: 7,260
    House size:
    Are you saying you are building a house that is 119' by 600'?
    I have never seen how the heatloss program you used works. But, are you saying that the heat loss program says that a room, 10' X 10' with one outside wall exposure, and the same room with 2 outside wall exposures and a third room with three outside wall exposures all have the same heat loss values?
    If so, and you have a cat, and the program is on paper, use it to line the bottom of your cat box. It doesn't work that way. At least I've never seen it work that way. Though, it might work for you.
  • johnny1234
    baseboard boiler size
    first floor 7 rooms
    5x5x9 powder room 1windowbtu675
    kitchen22x14x9btu1window4336btus
    study12x14x91window4536btus
    foyer10x14x20frontdoor7200btus
    off kit eat in10x17x9french doors4590 btus
    livingroom 15x8x94050btusbay window
    din room18x14x97290btus2 windows
    fam room20x14x98100btus
    2nd floor
    bedroom14x14x91window5292btus
    bedroom15x14x91window5670btus
    bedroommaster18x14x97560btus1window
    walk in closet 7x10x91890btus
    masterbath14x11x94158btus1window
    bath8x5xx91296btus1window
    3000
    sq feet
  • furnacefigher15
    Johnny1234
    First off. Only press the submit button once.
    Second. Square footage / cubic footage is only part of the calculation.
    Do yourself a favor and consult a qualified heating pro in your area. At the very least pay them or an engineer to spec what size heating equipment and baseboard you need.
    Would you try to guess at what size I beam to use to hold up the floor over a 30 foot span? I wouldn't either.
    I know you want to save some money, but a job done wrong will cost 10 times more to fix later, then it will to just do it right now.