air problem
shorti
Member Posts: 10
Just installed a new boiler. One of the zones t-stats will not get up to temperature. There does not seem to be much temp drop across supply and return. Almost seems like the heat is not transferring. Tried purging numerous times. The loop has approx. 30' baseboard and an 8400 BTUH kickspace heater. The feed and return piping seems very hot everywhere. The boiler runs to limit shuts down, cools, and runs back to limit. Is it air? Driving me nuts.
Is
that loop 1/2" copper or pex?0 -
shorti
3/4 pex0 -
shorti
3/4 pex0 -
Are
the baseboards getting hot, and the kick-space heater blowing hot?0 -
shorti;'s air problem
They are warm but I don't think they are as hot as they should be.0 -
Got pictures??
Purging is different for each system...
ME0 -
shorti air problem
here is a picture of the return side. The purges are built on the isolation flange above the pump and the bottom side of the pump are isolation flanges with flo checks built in. Maybe I need more pump? I calculate my approximate load @ 32,000 btuh. 3.2 GPM @ 7.8'. The 007 should take care of this.0 -
Missing valve...
You MUST purge THROUGH the pump. Pumps with integral checks are very subject to air binding, partial or completely.
If you have one more ball valve between the boiler and the common return, you'd be able to purge through the lower drain valve (purge cock).
No easy fix for your situation. If you could flip flop the iso flange with the purge flange, you stand a better chance of at least getting the pump completely purged.
Another thing to try, quickly close the iso flange with just that pump running, and see if you can hear a HISSSsss as the valve closes off. If no, then it is not moving (much) water. If yes to the hiss, then it indicates it is moving water.
ME0