Leaking Backflow Preventer
a2shutt
Member Posts: 97
Hi, I've got a Conbraco backflow preventer on the water feed to my boiler. It drips out the bottom maybe every 3 seconds. I don't have any idea where to start in fixing this drip, and i want to make sure that it isn't indicative of failure...perhaps leading to drinking water contamination.
Anyone have any tips on fixing these?
I think the model number is 40-203-02.
Thanks,
Aaron
Thanks,
Aaron
Mine drips a bit too
Not sure if this is normal.0 -
Not sure
but I think that model is a reduced pressure zone valve with a relief vent. If the relief vent is dripping -- which sounds like what you are describing -- it means that one of the two check valve assemblies is leaking.
And should be replaced; I'm not sure it's repairable. Sorry about that.Br. Jamie, osb
repair kit
Conbraco Model #40-203-02 has a repair kit no. 40-003-940 -
Re: leaky backflows
A lot of the time it just needs flushing out. Pull checks out below square headed caps and clean off bottom of plastic plunger where rubber gasket is. Flush out receiver ports and put check (s) back in. Most of the time it is debris under the check seats. Needs to be done by someone who understands how to shut off water flow to it and backflow construction or you will have problems. Also if you do not put back in correctly they will be problems.0 -
Thanks
I'll look into flushing it out and if that doesn't work, I'll get the repair kit.
Shutting off the water seems straightforward, as there is a ball valve on either side of the valve body. I'll do some research and find out how those work. I'm as smart as any plumber
backflow
Installing a brass wye stainer ahead of backflow will keep backflow clean. Also on a job I had a backflow dumping water, found ruptured checks inside backflow (Febco 825y ) . Backflow was servicing a steam boiler in a 5 floor nursing home. Boiler was on roof and building had a terrible water hammer problem in the domestic water piping ( thats another issue ) I found that water hammering and a unusual press drop at inlet to backflow was causing damage to internal checkvalves. I installed a brass spring check valve ahead of the backflow, this took care of the problem untill the the water hammer issue is resolved.There was an error rendering this rich post.
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam
