water being pulled from boiler
roadrunner
Member Posts: 1
I have a 450 mills smith boiler ,2,500,000,btu 2 pipe condensate pump return that the water is pulled right out of the boiler and going off on low water.
Has this problem just started?
Has it always done this? If not have there been any changes to your system lately?
Is it piped properly? You may need to post a few pictures of the boiler and near piping if you're not sure.
Anything done with your boiler water lately? Could be foaming and priming?0 -
Need more info
Just trying to narrow things down a bit.
Does the water disapear, never to be seen again? (which would suggest a leak)
Or, does the water eventually make its way back to the boiler? (which would suggest pressure too high, or a condensate return problem)0 -
more questions
Does the water suddenly disappear? Does the system have a condensate tank and pump? Are there zone valves on any of the steam mains?Dave in Quad Cities, America
http://grandviewdavenport.com0 -
Disappearing water
I will assume the boiler has worked well in the past and nothing mechanical has been changed. The boiler water has three ways to get out of the boiler: Carryover from dirty water and surface tension, it can back out the bottom of the boiler through a defective check valve at the condensate pump and up the chimney if you have a leak in a section.
I have had a lot of good results by cleaning the water side of the boiler.
Good luck,
Tim0