water being pulled from boiler
roadrunner
Member Posts: 1
I have a 450 mills smith boiler ,2,500,000,btu 2 pipe condensate pump return that the water is pulled right out of the boiler and going off on low water.
0
Comments
-
Has this problem just started?
Has it always done this? If not have there been any changes to your system lately?
Is it piped properly? You may need to post a few pictures of the boiler and near piping if you're not sure.
Anything done with your boiler water lately? Could be foaming and priming?0 -
Need more info
Just trying to narrow things down a bit.
Does the water disapear, never to be seen again? (which would suggest a leak)
Or, does the water eventually make its way back to the boiler? (which would suggest pressure too high, or a condensate return problem)0 -
more questions
Does the water suddenly disappear? Does the system have a condensate tank and pump? Are there zone valves on any of the steam mains?Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Disappearing water
I will assume the boiler has worked well in the past and nothing mechanical has been changed. The boiler water has three ways to get out of the boiler: Carryover from dirty water and surface tension, it can back out the bottom of the boiler through a defective check valve at the condensate pump and up the chimney if you have a leak in a section.
I have had a lot of good results by cleaning the water side of the boiler.
Good luck,
Tim0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements