Hydronic Air Vents
Zman
Zman Member Posts: 7,611
I have been spending quite a bit of time in medium sized commercial boiler rooms lately. I have been noticing that the majority of the air vents are closed (isolated with a ball valve). I may be peaking into Pandora's box here but, is there a reason for this?
I have always left the vent open figuring if air is in it wants to get out. Why not let it?
My question is, was the vent leaking and someone just closed it rather that fix it or is there a logical reason for closing them?
Albert Einstein
  • furnacefigher15
    furnacefigher15 Member Posts: 514
    compression tanks
    Systems with compression rather then diaphragm style tanks, can't have open auto vents. b/c the the air in the tank will eventually absorb into the water in the tank, and then if there is an open auto vent, then it will escape the system. When that happens, you'll feed more water into the boiler, and into the tank eventually water logging the tank.
    If the vents are left closed, then the reabsorbed air will come out of solution when the boiler water is heated, and then go back to the tank where it belongs, so long as it's piped right. Usually the tank is connected to an air separator of some kind.
    The air vents were probably put in for initial system, and service related air bleeding.
  • Zman
    edited January 2012
    1
    Albert Einstein
  • Zman
    Thanks for the reminder
    One of the systems was originally that  open tank type. I was converted at some point. The others were newer systems with diaphram type tanks. The primary air auto vents were closed
    Albert Einstein
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,874
    Foaming A.V.'s
    I have had some systems, that when first started, would leak water profusely from the A.V.'s Once all air had been removed, they eased vomiting, and their caps were left loose.
    On bladder/diaphragm type tanks, the A.V.s should be left open. If they leak constantly, they have debris under their seats and need to be cleaned/serviced.
    As FF noted, if it is a compression tank, all A.V.s MUST be closed to avoid removing the air that is compressed. Otherwise, you will end up with a whole new set of problems pertaining to pressure stability and leaking pressure relief valves etc etc.
    If it doesn't leak in the on position, I'd leave it open. If it leaks, its a service call.
    ME
  • Zman
    Thank You
    Thanks Mark, That clears it up in my mind
    Albert Einstein