Options
steve_25
Member Posts: 36
Boiler water pressure issues , is there a gasket on mechanical connection at the onboard , pancake style expansion tank . Would like to isolate to check tank air charge. Water side , Fill pressure 15 lbs., when burner fires , within a few seconds 30 lbs. and relief does its job , burner off back to 15 lbs. any experience.
0
Comments
-
Expansion Tanks:
They'll be putting external Extrol type tanks on these boilers to solve this problem. Get a #30 tank and connect it to the system with a double hose connection. If the problem stops, you have a leaky tank.
Another expensive cost cutting idea gone expensive.0 -
Expansion Tanks:
They'll be putting external Extrol type tanks on these boilers to solve this problem. Get a #30 tank and connect it to the system with a double hose connection. If the problem stops, you have a leaky tank.
Another expensive cost cutting idea gone expensive.0 -
Just did this....
I had this issue w/ the same make/ model. Drained the boiler and disconnected the tank. Simple union. Added 15psi air through schreader valve back in. It has been good for a month. You can get the replacement tank.0
This discussion has been closed.
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements