Radiator vents with street elbows
ToddB
I have two radiators that are located so that installation and removal of vents is difficult (vent contacts the adjacent wall). In order to remedy the situation I have installed a 45 degree 1/8" street elbow at each radiator and then connected the vent. I using Hoffman 1A vents. The radiators are heating however the problem that I am finding is that the vents are accumulating some condensate. Do the 1A vents have to be vertical in order to work properly, or can I rotate the street elbows slightly to permit condensate to drain? Thank you.
Vents...
have floats in them, and need to be vertical or very very close to that to work properly. That said, you might be able to tweak them just a tad -- I can't see that much condensate would collect in a street elbow, though...Br. Jamie, osb
Hoffman 1A
I had this issue with one of my radiators and the Hoffman 1A. After draining the vent a few times I decided to swap it out for another new 1A. Since then I have not had any problems but mine are 90 degree to the radiator.
Another option may be a 90 degree street elbow with a Hoffman 1B. I believe a 1B is the straight equivlant to a 1A and is avaliable at pexsupply.com
I'm sorry if I'm way off, some pictures may help give us a better idea of what will work for you.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
dont understand what you are doing
Wouldn't a 45 st. el decrease the room you have even more, since it sticks out even further into the area between the radiator and the wall?0 -
Questions
I was thinking about switching to a 1B, but was unsure if it was the right application given the 1/4" NPT and that it is called a "convector" air valve. I suppose that I could use a 1/8" nipple and reducing elbow to install the vent. Do the 1A and 1B have the same venting rates on their 1 to 6 scales?0 -
1B
Not sure, but I can only assume the 1A and 1B are identical other than the 1B is intended for a convector.
I'd go for a 1/8" to 1/4" reducing elbow if you can find one and try it out. Chances are it'll work great. The 1-6 scale on the 1A is FAR from accurate. You can make it do almost any amount on just one setting by sliding the cap around horizontally. Its a shame too being its such a good vent otherwise.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Hoffman Vents
Hoffman vents that have a right angle connection, 1A, 40, etc., have a tounge that protrudes from the vent and is supposed to be hanging in free air inside the radiator. This device is desinged to draw the water out of the vent and prevent occumulation of water which causes the vent to spit. If the tounge is laying inside a horizontal pipe it cannot function correctly and the spitting of water and/or water logging of the vent that you're experiencing is to be expected.Dave in Quad Cities, America
http://grandviewdavenport.com0 -
Thank you
Thank you. That is exactly what I thought may be happening. It appeared that there was enough room for the vent's tongue to move, but I believe now that it may be impeded by the street elbow wall. The radiators do heat well, so I do not think that the condensate it having a large impact, but I do not like the idea of collecting water and potential spitting. I think that I may try the 1B with a revised connection method to play it safe.0 -
Remote the Radiatior Vent
Hi- I'm not quite sure where you are planning to go with this. A 1/8 inch pipe, size wise, has plenty of venting capacity ( almost enough to support a Gorton # 2 main vent ) so I don't see the benefit of going to a Hoffman 1 B. If the clearance is that tight, remote the vent away from the end to a location where you have suitable clearance by using a 90 degree street elbow, a nipple coming up at a 45 degree angle and a 45 degree elbow to get the piping back to the horizontal before attaching the Hoffman 1A. You could remote the vent 10 feet + away from the radiator and it would still work fine. You just need to slope it a bit so any water runs away from the vent. If you are getting excessive water then the problem is elsewhere and not at the vent.
- Rod0
- 109 Chimneys & Flues
- 5.6K Gas Heating
- 970 Plumbing
- 386 Solar
