Honeywell Controls
Bruce1971
Member Posts: 4
in Oil Heating
I have a Brunham V-14a-t boiler, Carlin head with honeywell controls. I replaced the vitrol water coil and temp/pressure guage in the spring and never really ran the heat since. I am curious to what my temps should be set at on the controller and also what the, I believe is the cycle control, should be set at. Since I changed the water coil, I have to keep my controls temp controls set much lower than before. The oil company service guy had them set at 140 low and 180 hi and the other knob set at 20. When I have them set there, my temp guage on the furnace gets up to 210 degrees before it shuts down. I think that may be too hi. Any ideas? Thanks.
honeywell aquastat
is probably what your talking about.i would set that hi limit to 160 ,and leave everything else alone.if your temp was reaching 210 you must heard some banging in the pipes.0 -
temps
You replaced the tankless coil? Side mounted coil? Long capillary R8182H Honeywell control? Is the remote bulb all the way in/bottomed out in the well? If that is the control that you have, it is not uncommon for them to be off close to 20 degrees. Do you have a mixing valve for the coil? If so, 165 low, 185 high, diff of 10, there is a fixed 5 degree differential in those controls, so 10 plus 5 will equal 15 degrees diff0 -
triple aquastat
The differential only applies to the low limit. The hi-limit comes into play on a call for heat and should shut the burner down at the setting, then reset after a 10 degree drop in temperature,that is built in, and has nothing to do with the differential. You either have a bad gauge( first choice), bad aquastat, or as stated, poor contact of the capillary tube.0 -
differential
failed to mention that it only applies to the low limit, thanks Paul. The differential has nothing to do with the over riding temp on the high limit side0
- 120 Geothermal
