Viessmann Boiler
DRK
DRK Member Posts: 2
Can a Viessmann Viodens condensing wall boiler be used to supply hot water for air handlers for hydro air. I don't seem to be making hot enough water. Thanks for any help.
  • CMadatMe
    CMadatMe Member Posts: 3,086
    edited December 2011
    Yes
    Do it all the time. Are we not making or are we not delivering enogh gpm to the airnhandler. More info please. Which Vitodens? What size air handlers? What is the heat loss of each a/h zone? What size pipe to the a/h's? What pump are you using for the a/h?
    Are we using a low loss header on the boiler? Are you running a 1.6 slope? If a 200 did we get the boiler out of nightine setback? Could ask dozens of questions.
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,584
    Max temp
    On the 100 and the new 200 is 176*,the older 200 is 167*
  • CMadatMe
    Received
    Your e-mail and sent you a reply. Need alot more info. Please provide it.
  • CMadatMe
    Hope
    The call helped out. Let me know how you make out changing that zone pump.