Viessmann Boiler
DRK
Member Posts: 2
Can a Viessmann Viodens condensing wall boiler be used to supply hot water for air handlers for hydro air. I don't seem to be making hot enough water. Thanks for any help.
0
Comments
-
Yes
Do it all the time. Are we not making or are we not delivering enogh gpm to the airnhandler. More info please. Which Vitodens? What size air handlers? What is the heat loss of each a/h zone? What size pipe to the a/h's? What pump are you using for the a/h?
Are we using a low loss header on the boiler? Are you running a 1.6 slope? If a 200 did we get the boiler out of nightine setback? Could ask dozens of questions.There was an error rendering this rich post.
0 -
Max temp
On the 100 and the new 200 is 176*,the older 200 is 167*To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
Received
Your e-mail and sent you a reply. Need alot more info. Please provide it.There was an error rendering this rich post.
0 -
Hope
The call helped out. Let me know how you make out changing that zone pump.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements