Viessmann Boiler

DRK
DRK Member Posts: 2
Can a Viessmann Viodens condensing wall boiler be used to supply hot water for air handlers for hydro air. I don't seem to be making hot enough water. Thanks for any help.

Comments

  • CMadatMe
    CMadatMe Member Posts: 3,086
    edited December 2011
    Yes

    Do it all the time. Are we not making or are we not delivering enogh gpm to the airnhandler. More info please. Which Vitodens? What size air handlers? What is the heat loss of each a/h zone? What size pipe to the a/h's? What pump are you using for the a/h?



    Are we using a low loss header on the boiler? Are you running a 1.6 slope? If a 200 did we get the boiler out of nightine setback? Could ask dozens of questions.

    There was an error rendering this rich post.

  • Robert O'Brien
    Robert O'Brien Member Posts: 3,562
    Max temp

    On the 100 and the new 200 is 176*,the older 200 is 167*
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • CMadatMe
    CMadatMe Member Posts: 3,086
    edited December 2011
    Received

    Your e-mail and sent you a reply. Need alot more info. Please provide it.

    There was an error rendering this rich post.

  • CMadatMe
    CMadatMe Member Posts: 3,086
    Hope

    The call helped out. Let me know how you make out changing that zone pump.

    There was an error rendering this rich post.

This discussion has been closed.