gas pipe sizing
Options
zepfan
Member Posts: 444
in Gas Heating
as a rule of thumb what diversity factor should be used when sizing a 2 psi gas pipe system? say for example you have (5) 130,000 btu input gas fired rooftop units,with a design day in the winter of 12 degrees.it is highly unlikely that all of these units would be firing at the same time.is there a diversity factor that should be used when sizing the pipe?any feedback would be much appreciated.thank you
0
Comments
-
Gas piping
By code, one should always size for the maximum BTU input of all appliances regardless if they only work part time or in the off season.0 -
In other words with
your application there is no diversity factor. Diversity factor would be having a pool heater for use in the summer time and a boiler for use in the winter.
There actually is the possibilty at some time they all would be firing.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements