bench test r7184U
chuck172
Member Posts: 90
I'm trying to troubleshoot my primary. I have the cad cell connected and seeing light, Line voltage to L1and L2.
The green light is on, but when I check for voltage at the Burner Motor connection, nothing.
T&T are jumped.
Shouldn't I be getting voltage to the burner motor here?
T&T are jumped.
The Cad Cell
should start out "in the dark" or disconnected.
The control should NOT start the burner motor if it thinks there is already a flame being detected.
Once the burner motor voltage is detected, then quickly connect the cad cell.All Steamed Up, Inc.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
cad cell
The burner motor does start with the cad cell disconnected. Then as soon as I connect the cad cell, the primary goes off on reset, the light starts flashing.0 -
lock out
If the control sees light/flame before oil valve is energized by the control. it will lock out. Why are you bench testing the control?0 -
why?
I'd like to know if my primary is shot and needs replacing.0