bench test r7184U

Options
chuck172
chuck172 Member Posts: 90
I'm trying to troubleshoot my primary. I have the cad cell connected and seeing light, Line voltage to L1and L2.

The green light is on, but when I check for voltage at the Burner Motor connection, nothing.

T&T are jumped.

Shouldn't I be getting voltage to the burner motor here?

Comments

  • Gordo
    Gordo Member Posts: 857
    edited November 2011
    Options
    The Cad Cell

    should start out "in the dark" or disconnected.



    The control should NOT start the burner motor if it thinks there is already a flame being detected.



    Once the burner motor voltage is detected, then quickly connect the cad cell.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • chuck172
    chuck172 Member Posts: 90
    Options
    cad cell

    The burner motor does start with the cad cell disconnected. Then as soon as I connect the cad cell, the primary goes off on reset, the light starts flashing.
  • billtwocase
    billtwocase Member Posts: 2,385
    Options
    lock out

    If the control sees light/flame before oil valve is energized by the control. it will lock out. Why are you bench testing the control?
  • chuck172
    chuck172 Member Posts: 90
    Options
    why?

    I'd like to know if my primary is shot and needs replacing.