Options
chuck172
Member Posts: 90
I'm trying to troubleshoot my primary. I have the cad cell connected and seeing light, Line voltage to L1and L2.
The green light is on, but when I check for voltage at the Burner Motor connection, nothing.
T&T are jumped.
Shouldn't I be getting voltage to the burner motor here?
The green light is on, but when I check for voltage at the Burner Motor connection, nothing.
T&T are jumped.
Shouldn't I be getting voltage to the burner motor here?
0
Comments
-
The Cad Cell
should start out "in the dark" or disconnected.
The control should NOT start the burner motor if it thinks there is already a flame being detected.
Once the burner motor voltage is detected, then quickly connect the cad cell.All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
cad cell
The burner motor does start with the cad cell disconnected. Then as soon as I connect the cad cell, the primary goes off on reset, the light starts flashing.0 -
lock out
If the control sees light/flame before oil valve is energized by the control. it will lock out. Why are you bench testing the control?0 -
why?
I'd like to know if my primary is shot and needs replacing.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 62 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements