Measuring Radiator Height
Rob_40
Rob_40 Member Posts: 59
Stupid question, but here goes:  When measuring a radiator's height to calculate the EDR, is it the distance from floor to top of radiator, or from bottom of column to top of column?   Seems like the space under the radiator should not be part of that measurement, but maybe its factored in to the equation.   Thanks in advance for any advice.
Rob
  • BobC
    BobC Member Posts: 5,539
    Floor up
    Measure from the floor up to the top.
    Bob
    3PSI gauge
  • Rod
    Rod Posts: 2,067
    EDR Measurements
    Hi Rob- Attached is a radiator sizing chart which I thought might be of help to you.  As you can see in the examples on the left side of the second page, the height measurement ,as Bob mentioned, is from the floor level.
    - Rod
  • Rob_40
    Glad I Asked!
    Thanks for your help, and the chart!
    Rob