burnham in5 install
jeeeepster
Member Posts: 3
Hi guys, I am installing a burnham in5 to my one pipe steam system. After reading the install manuals it looks like I can hook up my return piping and Hartford loop on either side of the boiler. Am I correct ?
My return piping in my house is copper which runs along the floor of my basement, I am changing the return piping near where it hooks up to the boiler(aprox. 8' away from Hartford loop) should this piping be done in black pipe?
Thanks for the help.
Burnham IN5 Return Tappings
Hi - Look on Page 6 of the IN-5 I&O manual on the subject of section tappings. You can use either "D" or "F" for the return port. Both are 2 inch tappings.
As for the return, you can do it in either black pipe or copper as it isn't a steam bearing pipe.
- Rod0 -
Joining Pipe
We use a brass fitting when transitioning from copper to steel pipe. It avoids corrosion.0 -
Corrosion
I would not say it eliminates corrosion, just slows it down a bit. I would wager that pipe dope or teflon tape will do more to prevent corrosion.
http://www.corrosionist.com/galvanic_corrosion_chart.htm0 -
galvanic corrosion
i think most of the problems were with galvanized iron pipe, joined to copper. the copper and zinc are very reactive with each other.--nbc0 -
Corrosion
It probably doesn't eliminate corrosion. Jobs we did thirty years ago show no corrosion at these connections. Anyone depending on Teflon tape to isolate two metals won't be in business for long, and won't pass an inspection in New York City.0
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam
