close call
steamy ray vaughn
Member Posts: 27
a customer called at 11:30 pm and said these exact words. My boiler is glowing cherry red and I think there might be something wrong
hehehe
he thinks??gwgillplumbingandheating.com
close call
The boiler actually cracked the concrete pad it was sitting on and melted the transformer0 -
close call
close call
WOW
Scary stuff...think I'd pull the plug and run...0 -
close call
Went there the next morning the safguard 400 did not shut down the burner and the 47-2 lwco feed combo float was laying on a mountain of mud. Cut in a bypass line to see if the vessel would hold nodice. the returns where 90% plugged. He has no idea how lucky he really was.0 -
Scarey Stuff
Run away dry firing is always scarey. Makes me wonder why no one ever thinks of mounting an acquastat set at 240F. It would shut the boiler down before any damage was done. Of courese, the cast might still crack, but there were be better protection against a building fire.Dave in Quad Cities, America
http://grandviewdavenport.com0 -
That is the
first time I ever felt a triple post was valid and even necessary. Kind of showed some emotion even tho it was a mistake..
I'm about to install a Safegaurd 400 on my own boiler. Is it common for them to fail like that?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Agree!
with you on the triple post!Dave in Quad Cities, America
close call
funny thing that the customer forgot to mention on the phone was that he had replaced the transformer prior to putting it into service. He told me that he is a car mechanic. I don't think I'll be taking my car to him in the near future0 -
radiator flush?
At least I would not let him to a radiator / coolant flush!
By the way..... qca= Quad Cities??Dave in Quad Cities, America
close call
yep Quad Cities0 -
Howdy
Nice to see someone on here from home.Dave in Quad Cities, America
hello
hello back at ya.0
- 120 Geothermal