taco 503 zone panel

the zone to my indirect hot water heater keeps turning on and off every couple of sec turning the circulator  on and off . changed the cube relay seemed to solve problem for a little while any suggestions on what is causing this.

Comments

  • lchmb
    lchmb Member Posts: 2,997
    aquastat

    Did you check your indirects aquastat? Wiring for lose connections?
  • smitty_6
    smitty_6 Member Posts: 6
    thanks

    jumped out the aqustat found it to be bad replaced it everything working fine now                