28 inches.
Options
ChrisJ
Member Posts: 17,070
When measuring to see if you have 28 inches from your NWL to the lowest steam carrying pipe I assume dry returns also count?
My issue is if I want to go with an IN5 it appears I might only have 27 inches to the end of one of my dry returns. The steam main is much higher obviously.
Will this cause a problem?
I'm having trouble getting a perfect measurment as the boiler is on a concrete slab while the dry return is over dirt. I may need to make a water level to be sure.
My issue is if I want to go with an IN5 it appears I might only have 27 inches to the end of one of my dry returns. The steam main is much higher obviously.
Will this cause a problem?
I'm having trouble getting a perfect measurment as the boiler is on a concrete slab while the dry return is over dirt. I may need to make a water level to be sure.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Comments
-
Should be OK
there was a bit of extra headroom in the 28-inch "A" dimension.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Numbers.
Your A Dimension technically only needs to be high enough to match the steam's pressure loss in the main, plus a little extra. If the boiler runs at 2 psi, and the steam loses 1/2 psi at the end of its run, you would need an additional 1/2 psi of pressure to push the condensate back to the boiler. 1/2 psi = 14 inches. But just adding another 1/2 psi would only equalize the supply and return, so to make sure that the condensate really gets pushed back into the boiler, we raise the A Dimension to 28. 28 inches = 1 psi. So now the return has 1/2 psi more pressure than the boiler (1-1/2 plus 1).
In other words....27 inches is fine. It equals something like 0.96 psi.0 -
Ah
So theoretically something like say, 20 inches should work under most conditions?
I'm curious, is there a way to calculate the pressure drop in a steam main?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Ummm.
A pressure gauge? I've never had the need to do it. If I had steam in my house, I would put a gauge at my main vent location just to actually see what it is. Supposedly, all/most/some/any? stream system should be sized for a 1/2 psi drop on the main. I know there's a way to calculate it but I'm sure it's in a book or chart somewhere that I just can't picture right now.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements