28 inches.
ChrisJ
Member Posts: 16,317
When measuring to see if you have 28 inches from your NWL to the lowest steam carrying pipe I assume dry returns also count?
My issue is if I want to go with an IN5 it appears I might only have 27 inches to the end of one of my dry returns. The steam main is much higher obviously.
Will this cause a problem?
I'm having trouble getting a perfect measurment as the boiler is on a concrete slab while the dry return is over dirt. I may need to make a water level to be sure.
My issue is if I want to go with an IN5 it appears I might only have 27 inches to the end of one of my dry returns. The steam main is much higher obviously.
Will this cause a problem?
I'm having trouble getting a perfect measurment as the boiler is on a concrete slab while the dry return is over dirt. I may need to make a water level to be sure.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Comments
-
Should be OK
there was a bit of extra headroom in the 28-inch "A" dimension.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Numbers.
Your A Dimension technically only needs to be high enough to match the steam's pressure loss in the main, plus a little extra. If the boiler runs at 2 psi, and the steam loses 1/2 psi at the end of its run, you would need an additional 1/2 psi of pressure to push the condensate back to the boiler. 1/2 psi = 14 inches. But just adding another 1/2 psi would only equalize the supply and return, so to make sure that the condensate really gets pushed back into the boiler, we raise the A Dimension to 28. 28 inches = 1 psi. So now the return has 1/2 psi more pressure than the boiler (1-1/2 plus 1).
In other words....27 inches is fine. It equals something like 0.96 psi.0 -
Ah
So theoretically something like say, 20 inches should work under most conditions?
I'm curious, is there a way to calculate the pressure drop in a steam main?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Ummm.
A pressure gauge? I've never had the need to do it. If I had steam in my house, I would put a gauge at my main vent location just to actually see what it is. Supposedly, all/most/some/any? stream system should be sized for a 1/2 psi drop on the main. I know there's a way to calculate it but I'm sure it's in a book or chart somewhere that I just can't picture right now.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements