On a residential A/C or heat pump
what is the advantage of using a TXV with no bleed port? It seems to me that being able to start the compressor under no load would be a better choice.
  • Techman
    Techman Member Posts: 2,143
    TXV
    The bleed port takes time to equalize the pressurers,so, no short cycling is allowed.Unless there is a hard start assembly.Some mfrg's do ,some don't. How many AC units  are  out there w/  a TXV and no start assist.? Most need that  compressor starting helper.
  • TonyS
    TonyS Member Posts: 849
    You bring up a good point
    I recently found out not all hard starts are the same after trying to use a SUPCO ptc on a reciprocating compressor with a TXV. Of course after it wouldnt start I went to their website and read their booklet. What a great primer on start kits http://www.supco.com/images/pdfs/AC%20Hardstarts%20Booklet.pdf
    I just dont see the reason why they dont use a bleed port TXV, most of the stats and control boards have a 5 minute restart wait and even if that wasnt enough time to fully equalize it would be a lot closer that a positive stop type valve. Is a positive stop TXV more efficient?
  • Ironman
    Ironman Member Posts: 7,755
    Non Bleed TXV
    A non bleed is somewhat more efficient. If you'll recall, about 15 - 20 years ago, several manufacturers were recommending the addition of a liquid line solenoid, not for pump down, but to stop liquid from being fed into the evap after the compressor shut off. That, coupled with a TDR on the blower, raised he efficiency about .05 S.E.E.R.
    A non bleed TXV also helps prevent refrigerant migration and liquid in the crankcase (or the accumulator) upon start up.
    Bob Boan
  • Techman
    edited August 2011
    Supco
    In the begining Supco and others pushed their products as "one size fits all" . NOT!!!!!!!!!!!!!!!.  The packages that the Supco Start Assist  and others ,came in DID NOT have microfared ratings on the paper work . So ,which one of these  [7 ] " fits all " do I need? Now adays,the package has the m/fd rating printed on them. You still have to look up the compressors proper size start capacitor and then match the "specific" Start Assist to the comp.But ,what do you do @ 5:01 when no one can tell you the needed m/fd rating?And you are lucky enough to have all 7 start assists on board! Which way do I go ?
  • Techman
    TonyS
    Hi Tony,the 3-5 minute time delay is  usually in the t'stat.So, on cond units w/ hi/lo press safetys there is [usually ] no time delay  safety when cycling on  the hi/lo  press switch. And another junky compressor bites the dust!
  • TonyS
    Thanks for the help
    here is a utube clip I think you guys will like.
    http://www.youtube.com/watch?v=jFFRpxFkpcM
  • JStar
    JStar Member Posts: 2,752
    Soooo...
    ...you can take the PTC out of a SuperBoost and wire it to its own potential relay to make it work better?