Inefficient compressor
Paul S_3
Member Posts: 1,288
What are the signs of a imefficient compressor??
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
347-692-4777
ASMHVACNYC.COM
Typically.
Abnormally high suction, and low discharge. The compression ratio will be very low.
If you suspect a weak compressor, you should pump down the unit to a low number on the suction side and watch the gauge for any movement. If a valve is bad, the pressure will feed back and the low side will rise.0 -
Inefficient comp
The leaking back of hi press to the low side is true w/ leaking/bad discharge reeds . What about bad/leaking suction reeds?Is this a scroll or a recip comp?0 -
scrolls
I've been told not to pump down using scroll compressors.0 -
Scroll pumpdown
Sure you can!!!!!!!!!!!!!!!!!!Been doing it for years ,20 -25 or so that is!0 -
scroll pumpdown
You can pump down a scroll as long s you do not pump it down into a vaccum.I herd if you pump it down into a vaccum it could arc and cause a burnout.0 -
Scroll pumpdown
There is a trick to a Scroll pumpdown,though!Out of the "box" a Scroll cannot be used on a pumpdown.0
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 161 Indoor-Air Quality
- 999 Plumbing
- 391 Solar
- 55 Water Quality
- 45 Industry Classes
