Inefficient compressor
What are the signs of a imefficient compressor??
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
  • JStar
    JStar Posts: 2,752
    Typically.
    Abnormally high suction, and low discharge. The compression ratio will be very low.
    If you suspect a weak compressor, you should pump down the unit to a low number on the suction side and watch the gauge for any movement. If a valve is bad, the pressure will feed back and the low side will rise.
  • Techman
    Techman Posts: 2,143
    Inefficient comp
    The leaking back of hi press to the low side is true w/ leaking/bad discharge reeds . What about bad/leaking suction reeds?Is this a scroll or a recip comp?
  • Del
    Del Posts: 52
    scrolls
    I've been told not to pump down using scroll compressors.
  • Techman
    Scroll pumpdown
    Sure you can!!!!!!!!!!!!!!!!!!Been doing it for years ,20 -25 or so that is!
  • don_9
    don_9 Posts: 395
    scroll pumpdown
    You can pump down a scroll as long s you do not pump it down into a vaccum.I herd if you pump it down into a vaccum it could arc and cause a burnout.
  • Techman
    Scroll pumpdown
    There is a trick to a Scroll pumpdown,though!Out of the "box" a Scroll cannot be used on a pumpdown.