hartford loop and equalizer on one pipe steam?
paul_81
paul_81 Member Posts: 27
Came across a one pipe steam boiler today without a Hartford loop and equalizer.  The Steam main rises 30" then travels the perimeter of the basement, sloping down.  When it gets back to the boiler, there is a tee, piping from bottom of tee drops down 4.5' to enter the bottom of the boiler, top of tee goes up 18" to a steam vent.  Should we take the time and expense to pipe in the hartford loop and equalizer?
Does a programmable thermostat set to one CPH also make sense?
  • ChrisJ
    ChrisJ Member Posts: 17,064
    edited July 2011
    Absolutely
    I am not a pro, but my understanding is you should ALWAYS have a Hartford loop and an equalizer.  Installing it will be cheaper than replacing the building and its owners should a leak develop in the return line.
    Steamhead Member Posts: 18,188
    If the boiler is very old
    it may have been installed before Hartford Loops were required. Make sure it has a good low-water cutoff on it- I've seen a few that didn't.
    Consulting
  • Paul Fredricks_3
    Paul Fredricks_3 Member Posts: 1,556
    sounds like
    There's no wet returns, so nothing for the Hartford loop to protect. Good near boiler piping would be a good thing, like a header and equalizer.