hartford loop and equalizer on one pipe steam?

paul_81
paul_81 Member Posts: 27
Came across a one pipe steam boiler today without a Hartford loop and equalizer.  The Steam main rises 30" then travels the perimeter of the basement, sloping down.  When it gets back to the boiler, there is a tee, piping from bottom of tee drops down 4.5' to enter the bottom of the boiler, top of tee goes up 18" to a steam vent.  Should we take the time and expense to pipe in the hartford loop and equalizer?

Does a programmable thermostat set to one CPH also make sense?



 

Comments

  • ChrisJ
    ChrisJ Member Posts: 16,317
    edited July 2011
    Absolutely

    I am not a pro, but my understanding is you should ALWAYS have a Hartford loop and an equalizer.  Installing it will be cheaper than replacing the building and its owners should a leak develop in the return line.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Steamhead
    Steamhead Member Posts: 17,387
    If the boiler is very old

    it may have been installed before Hartford Loops were required. Make sure it has a good low-water cutoff on it- I've seen a few that didn't.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Paul Fredricks_3
    Paul Fredricks_3 Member Posts: 1,557
    sounds like

    There's no wet returns, so nothing for the Hartford loop to protect. Good near boiler piping would be a good thing, like a header and equalizer.