Sizing cast iron radiators
McPhinn
Member Posts: 3
Hello,
We were referred to this site as the best place to get knowledgable advice for our problem.
We need help sizing hot water cast iron radiators for two rooms in a gutted renovation of a 120 year-old house. We have installed underfloor radiant pex tubing (staple-up) in most of the rest of the house. The water temperature from the new boiler will run at 140 degrees for the heating system. We will insulate thoroughly.
The two rooms that need radiators are each approximately 170 square feet. They are bedrooms that will be used as offices/guest rooms. Our plumber calculated the heat loss at 6,000 btu/hr for room #1, and 7,000 btu/hr for room #2. He has said the bigger the radiator the better, but we are concerned about weight and getting huge radiators up the stairs.
The radiator for room #1 will go on a wall that is 4' long. Will a 38" x 38" (15 section) x 8" radiator be sufficient for this room?
The radiator for room #2 will go under a window that is 27" high. How large a radiator will we need?
Much thanks in advance for your help,
McPhinn
McPhinn
do you know the EDR
of the radiators you are looking at?
failing that how many "columns" in each section? 2, 3...?Rob Brown
sizing cast iron radiators
Thanks, I do not know the EDR. We are shopping for old cast iron radiators on Craigslist or from local vendors, so we need to work with what is available. Is there a way to calculate the minimum (and maximum) size radiators that would be appropriate for each of the rooms?
Much thanks,
McPhinn0 -
rads
Room 1: A 15 section (2 1/2") 4 column 38" H would be too small (5737 BTUs), if you could find a 5 col 15 section, it would work better @ 6750 BTUs with a thermostatic rad valve.
Room 2: at least 22 sec of 5 col. 26"h again you want a little bigger and add a TRV, especially when mixing staple up heat with cast rads.There was an error rendering this rich post.
EDR Table
See the attached table. Multiply the square footage x 110, if you're using 140* water, to get the btu output.Bob Boan
Thank you all for sharing your expertise and advice, we can now search for the correct sized radiators!
McPhinn0 -
Radiators
Did you get them yet? I'm coming down today.
Thanks, Bob GagnonTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
WHat size are you looking for?
With the height and edr you need I could check my inventory.Cost is what you spend , value is what you get.
cell # 413-841-6726
HI,
We also want to calculate the BTU's generated from our old cast iron radiator. We are doing some renos in the kitchen and we need the space used by the cast iron. We are trying to replace the tube type radiator, for one at the wall or something similar that will use less space than the actual one.
The Tube Radiator contains 5 tubes, 12 sections. It is 8 inches wide, 3 inches long and Height is 20 inches.
The room size is 14X 13,5 X 9.
The actual cast iron is underneath a window. The plan is to convert that window into a door or patio door to access our newly built deck.
Would you have any suggestion?
We are trying to buy second-hand wall cast iron and we are a bit limited on what is on the market. What would be the smallest and the larger option to heat this room?
Thanks in advance for you advice!
Sandrine0
- 87K THE MAIN WALL
- 116 Chimneys & Flues
- 109 Geothermal
- 984 Plumbing
- 389 Solar
