American Standard A-3 Hydronic Boiler

SALBuild1
SALBuild1 Member Posts: 11
I have an American Standard A-3 hydronic boiler (circa 1954). When it was serviced last, the sheet metal flange that holds the burner on the front of the boiler was not secured correctly, in that it pinched the round access panel below the blast tube, so I can not clean out the burn chamber (and that round panel was wedged open, so the boiler has been running poorly). I need to remove the sheet metal flange and burner assembly to take off the round access panel. I have removed the two top bolts, but can not pull them out of the flange, nor screw them back in. I have not removed the bottom bolt yet.



My Questions:

Q1: Shouldn’t the bolts just come out? They screw into the cast iron boiler, yes?, so why can’t I screw them back in? AKA: How do I remove the flange and burner assembly?

Q2: There is a label stating not to use a vacuum to clean out the chamber, as it is Kaowool, so how do I get the carbon pellets out of the bottom?





The picture is sideways, with the flange to the left (the white blotch is the screw head- not a nut and stud), and the round access panel to the right, with the wingnut. I couldn't rotate the picture, it should be rotated 90 degrees clockwise.



Thanks for everyones help!

SALBuild

Comments

  • Steamhead
    Steamhead Member Posts: 16,796
    edited April 2011
    What they probably did

    was run bolts thru the cast-iron front plate and secure them with nuts. This is common when upgrading burners on older boilers. You'll have to remove the front plate from the boiler by removing the bolts at its perimeter.



    That "cleanout opening" was actually a secondary air inlet, since the DH-series burners that originally came with these boilers were very finicky and sometimes needed secondary air. With a modern flame-retention burner this is not needed, and we generally close and seal them, since this extra air lowers efficiency.



    The proper retrofit chamber for that boiler is a standard "bathtub" type made of Kaowool. The proper size depends on the exact boiler model. Not only does this make a very nice flame environment, but it doesn't use or need a secondary air inlet if used with a modern burner.



    The burner will need to be tuned with a digital combustion analyzer after any repairs or modifications are made.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • SALBuild1
    SALBuild1 Member Posts: 11
    Job completed Successfully.

    Thanks Steamhead.

    I finally figured out that there were nuts on the back of the faceplate, by reaching my hand in through the viewing window, so I was able to tighten them down.



    I also was wondering if that bottom round plate was an air inlet, but it has never been closed and sealed. I wonder if that is why we only have about 78% efficiency (and thus the reason that I want to replace the thing, as well as it being rated for 136 MBh in a 900 sq.ft house!- can't have too much heat in NH in 1954!)



    Now with it running for 12 hours, I agree that it probably needs tuning, but given that I want to replace it this spring/summer, I'd rather put the money towards the new system.



    It's still TBD- direct replacement boiler, condensing boiler or mod/con propane. Anyone know of a cost comparison calculator that takes into account boiler efficiency and fuel cost and BTU per fuel? There must be some on the web, but I don't even know what to search for.



    This all started because the blower to pump coupler disintegrated. Thought it was going to be a quick replacement, and grew into "well, while I'm in there" quick cleaning- that made the job take me all day. But it's finished, and we have heat again....but I never did get the carbon granules out of the chamber.



    Thanks again Steamhead for answering.
  • Alan R. Mercurio_3
    Alan R. Mercurio_3 Member Posts: 1,620
    edited April 2011
    comparison calculator

    [Anyone know of a cost comparison calculator that takes into account boiler efficiency and fuel cost and BTU per fuel?]

    Try the attached file.
    Your friend in the industry,



    Alan R. Mercurio



    www.oiltechtalk.com
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,512
    That file:

    I converted it to pdf. 
    Retired and loving it.
  • SALBuild1
    SALBuild1 Member Posts: 11
    Cost Calculator

    Thanks Alan and Dan,

    It will definitely help, but as a pdf, I can't actually use it (I can't input current data in the cells), so therefore Dan, can you just point me in the right direction as to where I can find it, or was there something wrong with the original link?

    Thanks so much. This forum has helped me out many times, thanks Dan, for hosting it!
  • Alan R. Mercurio_3
    Alan R. Mercurio_3 Member Posts: 1,620
    edited April 2011
    Sal

    Sal, shoot me an e-mail and I'll send you that file.

    alanmercurio@oiltechtalk.com
    Your friend in the industry,



    Alan R. Mercurio



    www.oiltechtalk.com