I was looking around
crash2009
crash2009 Member Posts: 1,478
 the internet for a company to come over and do a combustion analysis.  On one companys website I found a couple photo's of their recent boiler jobs.  For some reason, they didn't look quite right.  Because of not looking right, I didn't even call them.  Is there anything wrong with the way these boilers are piped? Wassup with all those dirt legs?
    Steamhead Member Posts: 17,808
    Good eye
    the headers on these re-branded Dunkirks are supposed to be 2-1/2", and you can see they are reduced to 2" at the skim tees.
    All Steamed Up, Inc.
    Towson, MD, USA
    Oil & Gas Burner Service
    Consulting
    Jamie Hall Member Posts: 26,049
    I may be missing something --
    I often do -- and I'm not familiar with the way Bryant's should be piped -- but I have to admit that those don't look bad to me.
    The dirt legs and assorted other places where one might expect an elbow, but instead have a T, are mighty handy when you want to flush out a bit of pipe...