Heat Timer Outdoor Weather Head
boiler_man
Member Posts: 21
Hi, I have a customer who has requested that I set some sort of differential to his heatimer outdoor weather head. He insists that when the weather is between cold and warm like we had (nyc) yesterday that the boiler should not be operating for heat on a regular schedule. The MPC Platinum is set for 55 day and 40 night. He believes that there must be some sort of control with a differential type delay so as not to activate the heat when the outdoor temperature falls below 55 for say 30 minutes. Please help!
1
PLC
Use a PLC to do this, I control a lot of things with PLC'sThere was an error rendering this rich post.
weather head differential
I believe the MPC has a differential of a degree or two to stop the control from short cycling. If the OD sensor is located on the North side of the building, you should be OK. Look into the Internet package since you already have a Platinum control. Between the room sensor averaging and the remote access, I am saving customers tons over a stand alone Platinum controller. All steam controls work off cycle times. They will cycle on every hour if the OD temp is below the WWSD. Without the space averaging feature, all steam cycling controls will overheat.0
- 50 Industry Classes
