Noritz tankless gas water heater
I sold a contractor a Noritz 199,000 BTU input TGWH and he installed it in his showroom as a live fired unit. What happens when the unit is done running and it stops making hot water the relief valve pops off and a little amount of water runs out of  the relief valve. They have high incoming water pressure and I told them to install a PRV unit to reduce pressure. He said no he likes high pressure. Then I suggested to install a small thermal expansion tank. Putting the expansion tank on the cold water inlet pipe to the TGWH would that keep the relief valve from popping?
  • Ironman
    Ironman Member Posts: 7,842
    That's Exactly...
    What I would have recommended and what inspectors are requiring on all water heaters connected to municipal water in our area.
    Bob Boan
  • bob eck
    bob eck Member Posts: 930
    when contractors in my area put in tank type electric or gas water heaters on public water systems they do install a thermal expansion tank but when they install tankless gas water heaters they do not put in a expansion tank because the only time the unit fires is when water is running through it and a faucet is open. I never was a relief valve on a tankless water leak except on this job where I know they have extremely high water pressure. thanks for the info
  • Ironman
    The Issue...
    It isn't the type of heater that causes the problem so much as the high water pressure combined with fast closing valves on clothes and dish washers, etc. Adding water hammer arrestors to these would also help.
    Bob Boan
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,875
    There are two sides to every...
    T & P relief valve. Are you sure its not a thermal release instead of a pressure release?
    Residual heat in a combustion chamber can rise up and cause the relief valves thermal sensing unit to see the heat and let some water out.
    Easy enough to figure out. Put a Slow Hand recording pressure gage on it and see what the max pressure you see will be. If it is within reason, the problem is not pressure.
    ME