Taco relay help
Options

Pietro
Member Posts: 1
I have a Laars mascot 2, 2 zones with taco 570 zone valves, 1 taco 007 circulator and a taco sr502 relay. Need help with the wiring please.
Thanks,
Pete
Thanks,
Pete
0
Comments
-
Question
What is your question? Do you have a wiring schematic?There was an error rendering this rich post.
0 -
Bad News...
Sorry to tell you but you have the wrong mult contol for your application.
SR relays are for multiple pumps- pump for each zone, not zone valves.
ZVC relays are for multiple zones using one pump and zone valves.
you would need a ZVC 403 control,
Here is a link to the Taco site and the ZVC control.
http://www.taco-hvac.com/uploads/FileLibrary/100-5.1.pdf0 -
Funny
Ha, I didn't read it close enough I guess. Eric is right, you need a ZVC 403. There is a way to get it to work but it may be more complicated than just getting the right unit for the application. Guess I better read closer.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 116 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 109 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 989 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements