Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Taco relay help
Options
Pietro
Member Posts: 1
I have a Laars mascot 2, 2 zones with taco 570 zone valves, 1 taco 007 circulator and a taco sr502 relay. Need help with the wiring please.
Thanks,
Pete
Thanks,
Pete
0
Comments
-
Question
What is your question? Do you have a wiring schematic?There was an error rendering this rich post.
0 -
Bad News...
Sorry to tell you but you have the wrong mult contol for your application.
SR relays are for multiple pumps- pump for each zone, not zone valves.
ZVC relays are for multiple zones using one pump and zone valves.
you would need a ZVC 403 control,
Here is a link to the Taco site and the ZVC control.
http://www.taco-hvac.com/uploads/FileLibrary/100-5.1.pdf0 -
Funny
Ha, I didn't read it close enough I guess. Eric is right, you need a ZVC 403. There is a way to get it to work but it may be more complicated than just getting the right unit for the application. Guess I better read closer.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 423 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 60 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 375 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 55 Job Opportunities
- 18 Recall Announcements