white-rodgers 36C97 Type 203 cross -ref
jrod
Member Posts: 4
in Gas Heating
Can anyone recommend a replacement for the neg pressure valve listed above
I did not get these from a
direct cross reference but I know they are negative pressure gas valves.
White Rodgers 36E66-302
Robertshaw 7200DERN-680
Honeywell VK 8115
What is the valve your looking to replace used on? That would be of some help. Most of these negative pressure gas valves we see on equipment today do not have an after market replacement but you must go direct to the supply house who sells the equipment and then hope they also stock parts. Otherwise you have to go directly to the Original Equipment Manufacturer (OEM)0 -
make and model update
The boiler make and model is Trianco Heatmaker Model HW-M2-130N0 -
I would get in touch
with Laars as they now handle Heatmaker.
What is your location?0 -
thanks for all your input
the job is located in Peekskill NY north of NYC0 -
Laars will be able to
get a replacemsnt for you.
I was up your way this past summer doing a week of training.0 -
resolution (I hope)
tim , thanks again for your assistance. I inherited this job because the homeowner is a friend. I was trying to help because the tech working on the boiler wasn't having much success. I'm told that he was actually in contact with the original designer of the boiler and even he couldn't help. My friend had no heat since thursday and was desperate so I took the hour ride to go have a look for myself. As I followed the flow charts it was time to check the gas pressure and lo and behold the burner fired when i flipped the switch back on ( didn't even want to disconnect the manometer) . I stayed for a few hours while the pipes thawed and burner cycled many times .Sometimes it's better to be lucky than smart, the other guy seemed to check all the right things. I think we'll order the gas valve just to be safe.0