piping diagrams
Irv
Member Posts: 95
Fellas,
looking to find the near boiler piping diagrams for a peerless boiler manufactured in 1986. Thanks
Peerless Diagrams
Hi Irv- What is the model number you are looking for?0 -
model
looks like JOTTW ( I)? 50S
thanks0 -
JOT-TW I&O Manual
Hi Irv- I think the model number probably is 150. The "S" designates it is for steam rather than hot water. Attached is the I&O manual for that model. I checked the piping diagram. It only has the configuration and the pipe sizes. There is nothing on riser height so maybe that's why we see marginal heights on older systems.
- Rod0 -
near boiler
Thanks Rod. Trying to figure out why I have wet steam
Irv0 -
wet steam causes
can you post some pictures of your present piping, so we can see what might be the cause?
a description of the symptoms would help too.--nbc0 -
piping
Rod,
Would you know how I go about posting pictures?0 -
piping
Actually I meant Nicholas!0 -
picture post
Irv,
To post a picture you just click the " File attachment "and browse to the files location on your computer; you can add more than one by going through that process as many times as you have pictures. Only jpg files or pdf documents can be uploaded.
3PSI gauge0 -
pictures
Fellas,
Here are pictures of the near boiler piping. From the waterline to the bottom of the horizional header is 28". Thanks0 -
Wet steam thoughts?
Fellas,
Anything noticeable in the piping pictures which would indicate wet steam?0 -
What size is the riser
from the boiler? Is there a bushing in the boiler tapping? What boiler size do you have? Is the return clear? And finally is your pigtail clean and clear inside?Cost is what you spend , value is what you get.
cell # 413-841-6726
piping
The boiler is a peerless Jottw150s with a max cap of 180000and the IBR is 135000. The boiler has a 1.25 nozzle.Just cleaned out the pigtail and its clear. Two mains on a one pipe system, one is 33' with two gorton#1 on a tree, the other side is 49' with 3 gorton #1 on a tree.
The return for the shorter side I can see and it gets warm. The longer one I cant find. One half of the longer main is uninsulated, and part looks like its pitched level.
What measurement were you referring to as the riser? From the top of the boiler housing? Let me know thanks.0
