piping diagrams
Irv
Irv Member Posts: 95
Fellas,
looking to find the near boiler piping diagrams for a peerless boiler manufactured in 1986. Thanks
  • Rod
    Rod Posts: 2,067
    Peerless Diagrams
    Hi Irv- What is the model number you are looking for?
  • Irv
    model
    looks like JOTTW ( I)? 50S
    thanks
  • Rod
    Rod Posts: 2,067
    JOT-TW I&O Manual
    Hi Irv- I think the model number probably is 150. The "S" designates it is for steam rather than hot water. Attached is the I&O manual for that model. I checked the piping diagram. It only has the configuration and the pipe sizes. There is nothing on riser height so maybe that's why we see marginal heights on older systems.
    - Rod
  • Irv
    near boiler
    Thanks Rod. Trying to figure out why I have wet steam
    Irv
  • nicholas bonham-carter
    wet steam causes
    can you post some pictures of your present piping, so we can see what might be the cause?
    a description of the symptoms would help too.--nbc
  • Irv
    piping
    Rod,
    Would you know how I go about posting pictures?
  • Irv
    piping
    Actually I meant Nicholas!
  • BobC
    BobC Member Posts: 5,570
    picture post
    Irv,
    To post a picture you just click the " File attachment "and browse to the files location on your computer; you can add more than one by going through that process as many times as you have pictures. Only jpg files or pdf documents can be uploaded.
    Bob
    3PSI gauge
  • Irv
    edited January 2011
    pictures
    Fellas,
    Here are pictures of the near boiler piping. From the waterline to the bottom of the horizional header is 28". Thanks
  • Irv
    Wet steam thoughts?
    Fellas,
    Anything noticeable in the piping pictures which would indicate wet steam?
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,430
    What size is the riser
    from the boiler? Is there a bushing in the boiler tapping? What boiler size do you have? Is the return clear? And finally is your pigtail clean and clear inside?
    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • Irv
    piping
    The boiler is a peerless Jottw150s with a max cap of 180000and the IBR is 135000. The boiler has a 1.25 nozzle.Just cleaned out the pigtail and its clear. Two mains on a one pipe system, one is 33' with two gorton#1 on a tree, the other side is 49' with 3 gorton #1 on a tree.
    The return for the shorter side I can see and it gets warm. The longer one I cant find. One half of the longer main is uninsulated, and part looks like its pitched level.
    What measurement were you referring to as the riser? From the top of the boiler housing? Let me know thanks.