Increasing main venting
My mains (2 1/2", 45 ft., parallel flow) are vented through a 1/4" tapping at an elbow.  To gain increased venting, can I go to 1/2" vents through a 1/4" nipple and then a 1/4" x 1/2" reducing coupling?
  • BobC
    BobC Member Posts: 5,539
    1/4" CFM
    That main contains about 1.5 cu ft of air. I'm guessing a 1/4 tapping will be good for 2CFM at 2oz of pressure so it should work.
    The table I'm using lists a 1/8" pipe as good for 2cfm and a 1/2' pipe as good for 3.4cfm at 2 oz (Greening Steam pg131). There is nothing for 1/4' pipe and I assume the 1/8" figure is actually for the 1/4' pipe. Does anybody know if my assumption is right??
    Bob
    3PSI gauge
  • NJSteam
    NJSteam Member Posts: 6
    Gorton D
    Could I use one Gorton D on each main or is it necessary to use several in an antler?
  • BobC
    Gorton #2
    if each main is 45 ft of 2-12" pipe you need more venting than one or two Gorton D's; you would want a Gorton #2 on each one. More would not help because of the 1/4" tapping your coming through.
    Bob
    3PSI gauge
  • NJSteam
    Thank you
    OK, BobC, many thanks for your help.