Increasing main venting
NJSteam
Member Posts: 6
My mains (2 1/2", 45 ft., parallel flow) are vented through a 1/4" tapping at an elbow. To gain increased venting, can I go to 1/2" vents through a 1/4" nipple and then a 1/4" x 1/2" reducing coupling?
0
Comments
-
1/4" CFM
That main contains about 1.5 cu ft of air. I'm guessing a 1/4 tapping will be good for 2CFM at 2oz of pressure so it should work.
The table I'm using lists a 1/8" pipe as good for 2cfm and a 1/2' pipe as good for 3.4cfm at 2 oz (Greening Steam pg131). There is nothing for 1/4' pipe and I assume the 1/8" figure is actually for the 1/4' pipe. Does anybody know if my assumption is right??
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Gorton D
Could I use one Gorton D on each main or is it necessary to use several in an antler?0 -
Gorton #2
if each main is 45 ft of 2-12" pipe you need more venting than one or two Gorton D's; you would want a Gorton #2 on each one. More would not help because of the 1/4" tapping your coming through.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Thank you
OK, BobC, many thanks for your help.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements