Calculating equivalent head with in floor
Rankin
Member Posts: 23
I'm a little unfamiliar doing all my own calculations for a job and I need to replace a pump on an in floor system that doesn't appear to be putting out enough volume. When I'm calculating my total head, is the total cumulative of all the loops, or only as big as the greatest restriction.
Example: 1/2" pex at 1.5 GPM creates about 4.99' of head loss for every hundred feet. If I had four loops at 200' would I have a total of 39.92'H (4.99 x 2 x 4) or just 9.98'H (4.99 x 2) ?
Also, I was taught 2 to 4 feet per second is an ideal flow, I know the problems created by having too high of a velocity, but if it's less than that, would that it create too large a ^T?
Thank you, thank you!
Head Loss...
Is determined by the longest loop + the manifold, supply & return, any mixing or zone valves, etc. The second half of your example is right. See the link to a recent thread below.
http://www.heatinghelp.com/forum-thread/133286/Calculating-manifold-headlossBob Boan
trigger finger
Guess I should be making better use of this "search" function Dan has given us. Thanks0
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 161 Indoor-Air Quality
- 71 Pipe Deterioration
- 999 Plumbing
- 392 Solar
- 55 Water Quality
- 46 Industry Classes
