Hitting a wall on old system
I thought I'd have this old system up and running by replacing the relay control. I wired and rewired half a dozen times without any response from the system.
By jumping the Y and R terminals I can get the system to open the vent, start the gas, ignite via electric ignition. No pump action and certainly not safe, I just wanted to see if there was anything working at all.
That's the only way I can get ANY response out of this one. I'm just stumped.
Included is the Wiring Diagram off the front of the boiler and a diagram I drew while stumped that shows how I have it wired.
Thanks so much....
Tom
  • Ironman
    Ironman Member Posts: 7,898
    Bad Holding Coil
    The coil is bad in your relay. Double check that your wiring matches your diagram. It's correct, but I would move the wire on relay terminal 4 to connect to R" instead of "G" if your boiler short cycles at all. (Has to do with current draw through the heat anticipator).
    Replace your relay.
    Bob Boan
  • fatty_2
    fatty_2 Member Posts: 54
    ty
    thanks ironman, I also thought it was the relay so this is a problem i've had after replacing it. I'll try switching to the 4 to the R
  • fatty_2
    Also...
    Since the relay is new - is there a method of testing it with a multimeter that would prove it has gone bad... I really don't want to order another one and wait for it. It's getting to be a very cold jobsite.
  • Del
    Del Member Posts: 52
    edited December 2010
    run 24V through the coil
    and see if the relay contacts pull in (test for continuity) 0 resistance, you are closed and infinite you are open.  My meter has a continuity tester that beeps, maybe yours does too. When the contacts pull in, you should have 24V at the ignition control...I believe between terminals 2 and 6, and 120v at circulator. If you are not getting that, something is up. Double check the relay.....make sure it is the right type DPST.  Could also be a bad transformer, or loose hot or neutral wiring somewhere.  Make sure there is 120V at the transformer, and 24V coming out of it.  Hope you can fix it!
  • Ironman
    Testing
    Your transformer is good because it energizes the ignition. If you jumped "R & G" and nothing happened, the holding coil in the relay is bad. If it brought the system on, then your thermostat or its wiring is bad.
    Bob Boan
  • Del
    If you're
    In a bind, just get a relay box to control the circulator and use the end swith off the relay box to control the boiler. Are you sure there is not a low limit control in there? That could be why the circulator does not turn on right away.