LOOKING FOR A BOILER
humhead
Member Posts: 22
for my one pipe steam system. I have 376 sq feet of EDR. I had some contractors come in they have spec'ed units that have EDR ratting over 450. What would be a probably sized boiler for my house. All my mains are well insulated and there are no missing radiators. I can account for every riser coming off of my mains. I currently have a 26 year old oil fired Weill mclain. It is rated at 431 feet of EDR. I am converting to gas, so I need a gas steam boiler. I am not particularly loyal to any one brand, I am just looking for the right sized boiler.
Thanks
Thanks
sizes are not that specific
I am guessing you were quoted an Independence from Burnham as that is the smallest size that is above your edr. The next down would be too small. The installation is what makes the job on steam even more than the boiler, within reason.Cost is what you spend , value is what you get.
cell # 413-841-6726
Two of the most efficient gas-fired steamers:
Smith G8-S-4 at 413 square feet EDR
Slant/Fin Intrepid TR-30 with gas burner, at 421 square feet EDR
Both can be down-fired a bit if need be.All Steamed Up, Inc.
Consulting0 -
Weil mclains boilers
- seem to be popular in my area. One contractor spec ed the eg-50 which I thought was kind of large. The EG- 45 looks like a better fit. Also got a bid for a utica PEG 187C. I guess everyone wants to go up a section with my boiler. I don't want my boiler to short cycle. Am I being paranoid, or are my concerns justified? My steamer does a good job of heating my 1920's house, since I installed blow-in insulation and replaced all of my vents for the whole house. Before the insulation and the replacing of the radiator vents, the boiler would run a long time. I know "STEAMER" is a big fan of wet based boiler with gas guns, but no one in Essex county NJ wants to install one. Also guys are pushing the Williamson boilers claiming they are the same as the Weil Mclains. I feel like that is a cheap marketing push. I am from hell's kitchen so I get suspicious easily of the Rosy sell job. thanks for your thoughts, any suggestions would be great.
- Thanks
0 - seem to be popular in my area. One contractor spec ed the eg-50 which I thought was kind of large. The EG- 45 looks like a better fit. Also got a bid for a utica PEG 187C. I guess everyone wants to go up a section with my boiler. I don't want my boiler to short cycle. Am I being paranoid, or are my concerns justified? My steamer does a good job of heating my 1920's house, since I installed blow-in insulation and replaced all of my vents for the whole house. Before the insulation and the replacing of the radiator vents, the boiler would run a long time. I know "STEAMER" is a big fan of wet based boiler with gas guns, but no one in Essex county NJ wants to install one. Also guys are pushing the Williamson boilers claiming they are the same as the Weil Mclains. I feel like that is a cheap marketing push. I am from hell's kitchen so I get suspicious easily of the Rosy sell job. thanks for your thoughts, any suggestions would be great.
If you were in my area
You would be more than welcome to do my install. No one in north Jersey wants to do that kind of install. I have read your past threads and your jobs make a lot of sense. If you were in the North Jersey area your phone would be ringing. Since reading Dan's books I am a true disciple of steam. Any other idea's would be greatly appreciated. Thanks so much for working on this site.0 -
clammy?
isn't clammy in north jersey?1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
eg 50?
Eg 50 is to big like you said a eg 45 is the right size with a 21/2" drop header king vale return valve and some gorton #2 main hair vents and then you should be golden
im located in north nj0 -
drop header
a job i did in east orange. weil mclain eg 40 with 21/2" drop header0
