pressure buildup
NickyI
Member Posts: 3
I am working on a steam boiler that is building pressure within minutes of firing. It reaches almost 10 p.s.i. with in 15 minutes, and frankly i am stumped on what might be the problem. So far I have tried to clean the returns but have gotten no results from that. If anyone has any ideas about a possible cause that would be a big help. Thanks
What is it supposed to run at? Is this in your home? What is the pressuretrol set for?0 -
presure
The pressure is set to 1.5psi and yes it is a residential installation.0 -
Sounds like a clogged pigtail not shutting the boiler down. Could also be a bad pressure gauge, if that's where you're reading it from.0 -
thanks
Thanks for the suggestion ill give it a shot.0 -
as jstar said...
Is your boiler not shutting down when it gets to 1.5? Check pigtail first. Check working gauge second replce both as necessary. Send us pictures of your pressure controll tree please including inside of pressurtrol as best as possible.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
another thing...
Make sure that your pressuretrol spring isn't over compressed. It is possible to crank it too low thereby putting downwaard pressure on the sppring attached to the screw and messing it up. You shoul be able to see slight gaps within the coil.1-pipe Homeowner - Queens, NYC
- 87K THE MAIN WALL
- 116 Chimneys & Flues
- 109 Geothermal
- 984 Plumbing
- 389 Solar