Oil tank distance from burner
Bob Gagnon plumbing and heating
Member Posts: 1,372
What is the minimum distance in Massachusetts that we can put a boiler next to an oil tank?
Thanks, Bob Gagnon
Thanks, Bob Gagnon
CNR 4.00
Reading in the cmr 4.00 book it states unenclosed tanks min. 5 feet from any fire or flame either in or external to any fuel burning appliance.. this is for larger than 10 gallons hope this helps. firedragon ent. has some good books on the code in ma. Tim0 -
is it.....
Is this a residential application?
Not sure about Mass.,but in NJ a residential tank has to be at least 5' ft away from any fire or flame either within or external to any fuel-burning appliance (06 IRC M2201.2.1). If Mass. is using the International Codes you may want to refer to the IFC (International Fire Code) Chapter 6 and 34.
Robert O'Connor/NJ0 -
Thanks
for the quick reply, it is a residential application.
Thanks again, Bob GagnonTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
ten feet
is what I was told but I need to find it in writing.Cost is what you spend , value is what you get.
cell # 413-841-6726
5 feet
anything less, you can build a fire wall0 -
Thanks Bill
I am glad I am not 21 anymore, was it 10 feet years ago or was my chain being yanked back then?Cost is what you spend , value is what you get.
cell # 413-841-6726
distance
As long as I can remember Charlie, it was always 5 feet away. I have gotten a lot closer by building a fire wall.0