trouble with baseboard
mike638
mike638 Member Posts: 1
just installed baseboard heating in house when zone 1 calls for heat zone 2 also gets hot someone told me to add check valves so water does not get pulled from one zone to another is thi true
  • Big Ed_4
    Big Ed_4 Member Posts: 3,224
    edited April 2010
    Flow Control Valves
    Hot water will rise into the other zone .…
    Cooler water is more dense then Hot water ,so the hotter water will rise and the cooler water will fall , creating a flow up the supply riser ... It is called a gravity flow...
    You need to use flow control valves when running multiple zones or if the boiler is maintaining a temperature...
    Flow control valves control the direction of flow and counter the gravity forces .…
    Flow Control Valves = weighted flow valves , spring loaded check valves and zone valves ...
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,417
    Could be a wiring issue
    any photos you have of the install could help. Flow Checks can help. did the pumps have IFC in the model number? Is it zoned by pumps or zone valves?
    cell # 413-841-6726
  • Timco
    Timco Member Posts: 3,040
    pump location
    I have found systems where return mounted pumps shove water into the supply manifold and the water takes the path of least resistance to get back to the return manifold. Again, IFC pumps, under-slung return lines, spring / flow checks, and so on will fix this. Good near boiler piping practices ensure this does not happen and is the mark of a real pro.
    Just a guy running some pipes.
