How many loops on a manifold??
Kungur
Member Posts: 49
As I start my retro-fit of my house I have the 2nd. floor tubing and transfer plates in. Insulation tomorrow.
My question is when I do my 1st. floor. I will have 12 loops and would like to know is there a maximum # of loops that can realistically be on one manifold?
That Is Dependent
On head loss and whose manifold. For instant a Wirsbo TrueFlow Manifold can handle up to 12 loop configurations.There was an error rendering this rich post.
These are the ones
I was thinking of using Everhot (part# SSM010) or a Wirsbo TruFlow Jr.0 -
It is limited by....
The size of the manifold, AND the size of the supply/return lines serving the manifold, which ever is lesser.
For example, if you are using a 1-1/4" bodied manifold, but are only supplying it with a 3/4" S&R, then your max flow is limited by the S&R lines. If 3/4" can carry 4 GPM, and each branch circuit can carry 1/2 GPM, then the 3/4" lines dictate not more than 8 ports.
So, as with ALL hydronic questions, the only correct answer is, it depends....
Have you done a heat loss calc yet? That is what REALLY drives the S&R line size for the area being served. Manifold sizing is secondary to that.
ME0 -
it's about flow
not about loops. if you don't know your flow then you're guessing.
I've done 16+ loop manifolds. but I design low flow systems, so my feeds and the manifold body can take that, no problem.Rob Brown
in beautiful Rockport Maine.0
- 110 Chimneys & Flues
- 981 Plumbing
- 387 Solar
