BTU of plain copper pipe
Jfonto
Jfonto Member Posts: 43
Can anyone refer me to a chart with the amount of heat unfinned copper pipe radiates?
  • Jean-David Beyer
    Heat loss from copper tubing...
    There is a nice graph in John Siegenthaler's book, Modern Hydronic Heating, 2ND Edition, page 242. Figure 8-44. This applies for cases where the length of the tubing (in feet) divided by the flow rate (gallons/minute) is less than 20 ft/gpm. There is a complicated formula for when it is greater than 20.
    The graph has the temperature of the water - temperature of the air in degrees F = 0 at the left and 140F at the right. At the left end, the heat loss is zero. At the right is the heat loss at 140F difference. There is a separate curve for each size tubing.
    For example, at that end,
    Tube size     Heat Loss
    2"                 about 150 BTU/hr/ft
    1.5"               118
    1.25"              102
    1"                   85
    3/4"                 68
    1/2"                 52
    The lines are nearly straight.
  • TonyS
    TonyS Member Posts: 849
    Burnhams heating helper
    page 48     http://www.burnham.com/PDF/htghelper.pdf
  • Well JD is helping,,,
    anyway,, I was "crappy" to him before, and for that I`m sorry,,,, but I think we understand each-other now. ;-)
    PS- He gave some pretty valuable stats, (until you found the Burnham site) :-).