Can anyone refer me to a chart with the amount of heat unfinned copper pipe radiates?

Comments

  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    Options
    Heat loss from copper tubing...

    There is a nice graph in John Siegenthaler's book, Modern Hydronic Heating, 2ND Edition, page 242. Figure 8-44. This applies for cases where the length of the tubing (in feet) divided by the flow rate (gallons/minute) is less than 20 ft/gpm. There is a complicated formula for when it is greater than 20.



    The graph has the temperature of the water - temperature of the air in degrees F = 0 at the left and 140F at the right. At the left end, the heat loss is zero. At the right is the heat loss at 140F difference. There is a separate curve for each size tubing.



    For example, at that end,



    Tube size     Heat Loss

    2"                 about 150 BTU/hr/ft

    1.5"               118

    1.25"              102

    1"                   85

    3/4"                 68

    1/2"                 52



    The lines are nearly straight.