riello burner
eyeball
eyeball Member Posts: 3
i have a riello mec 3ka burner looking for service booklet went to riello website couldn't find anything . unit was running fine until it was switched to powervent from old chimney.burner producing to much smoke .any help would be greatly appreciated.
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,584
    That burner
    was discontinued over 25 years ago,time for an upgrade! You aren't trying to use your  eyeball to adjust this are you,Eyeball?
  • heatboy
    heatboy Member Posts: 1,468
    If I had to make a guess.....
    ....I would say the venter is the issue.  Riello burners work their best when firing into a positive pressure chamber area.  The venter may be causing an excessive draft.  What boiler is the burner attached to?  Lining the chimney is, by far, the better option if it can be done.
  • eyeball
    riello burner
    burner is on a burnham boiler chimney had to come down
    Steamhead Member Posts: 18,205
    edited March 2010
    Heatboy is on to something
    check the draft. Too much draft will pull the flame right off the burner head (we call it "loss of retention") and cause a smoky fire.
    Is there a draft regulator between the boiler and the power venter? What size is it? What size is the breech (flue outlet) on the boiler? What is the draft at the breech? What model Burnham is it?
    BTW, according to Firedragon, there are only detail differences between the Riello MEC and 40-series burners. I don't have his books in front of me to get the specifics though.....
    Consulting
  • Paul Fredricks_3
    Paul Fredricks_3 Member Posts: 1,556
    Nope
    There is a big difference between those 2 burners. A complete remake of the burner. The Mectron which came out after the MEC is similar to the 40 series.
  • Matthew Grallert
    Matthew Grallert Member Posts: 109
    edited March 2010
    That Old MEC
    Didn't they stop with the MEC in 1972 or so.  I've not seen another burner run as long or as well for anywhere near that long.  Great burner, that said it's time I think to replace that old jenny.  It doesn't owe anyone anything:-)
    Peace
    Matthew
    Now I wonder If I have a copy of the manual for one of those.  I'll check tonight.
    If I do I'll copy it for you.
  • toilburn
    toilburn Member Posts: 44
    toilburn
    Yes the burner should be replaced, but I know of at least 15 still running fine.
